I am trying to configure a GSM-Module with Elipse scada using elipse gsm driver.
The driver got configured but I can only send SMS once, If I try again, Nothing happens. To send another SMS, I have to restart Elipse Application.
Your help is needed to resolve same issue.
I also want to know how to send multiple SMS to multiple mobile numbers using Elipse Scada .
Help required regarding elipse GSM driver connected to elipse SCADA
Hi Amol!
How exactly are you doing to send SMS in your application?
For testing purpose I just wrote small script on Button action . And given provision for mobile number entry & message as setpoints (STRING)
Driver log is also attached.
With this setup I can only send one sms to one user mobile number. And I don’t know what I am doing wrong but to send second sms , I have to restart the application .
I want to send multiple sms to multiple users
24/10/2015 07:52:40.097 (0F98) DRIVER Driver name: Driver ELIPSE GSM v2.0.2 (IOKitLib v2.0.37)
24/10/2015 07:52:40.097 (0F98) DRIVER IOKitLib version 2.0.37 of Aug 28 2014 08:55:05
24/10/2015 07:52:40.097 (0F98) DRIVER drvStartComm(0,0,0,0)
24/10/2015 07:52:40.187 (0F98) DRIVER Current configuration (30 parameters):
24/10/2015 07:52:40.187 (0F98) DRIVER - IO.GiveUpTries = 1
24/10/2015 07:52:40.187 (0F98) DRIVER - IO.Log.Enable = 1
24/10/2015 07:52:40.197 (0F98) DRIVER - IO.Log.Filename = ‘d:\gsmdriverlog’
24/10/2015 07:52:40.197 (0F98) DRIVER - IO.RecoverEnable = 1
24/10/2015 07:52:40.197 (0F98) DRIVER - IO.RecoverPeriodSec = 2
24/10/2015 07:52:40.377 (0F98) DRIVER - IO.Serial.Baudrate = 9600
24/10/2015 07:52:40.407 (0F98) DRIVER - IO.Serial.DataBits = 8
24/10/2015 07:52:40.407 (0F98) DRIVER - IO.Serial.Port = 2
24/10/2015 07:52:40.407 (0F98) DRIVER - IO.Serial.RTS = 2
24/10/2015 07:52:40.407 (0F98) DRIVER - IO.TAPI.PhoneNumber = ‘’
24/10/2015 07:52:40.407 (0F98) DRIVER - IO.TimeoutMs = 3000
24/10/2015 07:52:40.407 (0F98) DRIVER - IO.Type = ‘Serial’
24/10/2015 07:52:40.407 (0F98) DRIVER - 18 parameters with value = 0 were omitted
24/10/2015 07:52:40.417 (1B78) IOKIT INITIALIZING…
24/10/2015 07:52:40.417 (1B78) IOKIT INITIALIZED!
24/10/2015 07:52:40.417 (1B78) IOKIT Request handler enabled
24/10/2015 07:52:40.417 (1B78) IOKIT CONNECTING…
24/10/2015 07:52:40.417 (1B78) SERIAL Opening COM2:9600,8,NONE,1 …
24/10/2015 07:52:40.617 (1B78) SERIAL Port opened!
24/10/2015 07:52:40.617 (1B78) IOKIT CONNECTED!
24/10/2015 07:52:40.710 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:40.710 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:40.710 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:40.710 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:40.710 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:40.710 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:40.710 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:40.710 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:40.710 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:41.734 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:41.734 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:41.734 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:41.734 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:41.734 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:41.734 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:41.734 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:41.734 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:41.734 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:42.734 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:42.734 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:42.734 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:42.734 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:42.734 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:42.734 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:42.734 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:42.734 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:42.734 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:43.734 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:43.734 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:43.734 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:43.734 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:43.734 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:43.734 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:43.734 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:43.734 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:43.734 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:44.741 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:44.741 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:44.741 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:44.741 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:44.741 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:44.741 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:44.741 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:44.741 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:44.741 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:45.741 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:45.741 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:45.741 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:45.741 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:45.741 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:45.741 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:45.741 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:45.741 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:45.741 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:46.741 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:46.741 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:46.741 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:46.741 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:46.741 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:46.741 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:46.741 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:46.741 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:46.741 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:47.021 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:47.021 (1B78) IO TX: AT+CMGS=“9769747727”[0D]
24/10/2015 07:52:47.051 (1B78) IO RX: [0D][0A]>
24/10/2015 07:52:47.051 (0F98) TAG ==> (0.037) Tag(6.0.0.0).WriteValue (07:52:47.027) ‘9769747727’ = SUCCESS
24/10/2015 07:52:47.751 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:47.751 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:47.751 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:47.751 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:47.751 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:47.751 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:47.751 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:47.751 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:47.751 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:48.751 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:48.751 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:48.751 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:48.751 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:48.751 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:48.751 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:48.751 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:48.751 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:48.751 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:49.751 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:49.751 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:49.751 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:49.751 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:49.751 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:49.751 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:49.751 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:49.751 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:49.751 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:50.751 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:50.751 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:50.751 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:50.751 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:50.751 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:50.751 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:50.751 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:50.751 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:50.751 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:51.651 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:51.651 (1B78) IO TX: test sms[1A]
24/10/2015 07:52:53.811 (1B78) IO RX: [0D][0A]+CMGS: 96[0D][0A][0D][0A]OK[0D][0A]
24/10/2015 07:52:53.831 (0F98) TAG ==> (2.182) Tag(5.0.0.0).WriteValue (07:52:51.587) ‘test sms’ = SUCCESS
24/10/2015 07:52:53.831 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:53.831 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:53.831 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:53.831 (1B78) IO TX: AT+CMGF=1[0D]
24/10/2015 07:52:53.851 (1B78) IO RX: [0D][0A]OK[0D][0A]
24/10/2015 07:52:53.861 (0F98) TAG ==> (0.028) Tag(0.0.0.0).WriteValue (07:52:51.684) 1 = SUCCESS
24/10/2015 07:52:53.861 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:53.861 (1B78) IO TX: AT+CMGF=1[0D]
24/10/2015 07:52:53.881 (1B78) IO RX: [0D][0A]OK[0D][0A]
24/10/2015 07:52:53.881 (0F98) TAG ==> (0.027) Tag(0.0.0.0).WriteValue (07:52:53.846) 0 = SUCCESS
24/10/2015 07:52:53.881 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:53.881 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:53.881 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:53.881 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:53.881 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:53.881 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:53.881 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:53.881 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:53.881 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:54.881 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:54.881 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:54.881 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:54.891 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:54.891 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:54.891 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:54.891 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:54.891 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:54.891 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:55.891 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:55.891 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:55.891 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:55.891 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:55.891 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:55.891 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:55.891 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:55.891 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:55.891 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:56.891 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:56.891 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:56.891 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:56.891 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:56.891 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:56.891 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:56.891 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:56.891 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:56.891 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:57.891 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:57.891 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:57.891 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:57.891 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:57.891 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:57.891 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:57.891 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:57.891 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:57.891 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:58.901 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:58.901 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:58.901 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:58.901 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:58.901 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:58.901 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:58.901 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:58.901 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:58.901 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:59.901 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:59.901 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:52:59.901 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:59.901 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:59.901 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:52:59.901 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:52:59.901 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:52:59.901 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:52:59.901 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:00.901 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:00.901 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:53:00.901 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:00.901 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:00.901 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:53:00.901 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:00.901 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:00.901 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:53:00.901 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:01.901 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:01.901 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:53:01.901 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:01.901 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:01.901 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:53:01.901 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:01.901 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:01.901 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:53:01.901 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:02.901 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:02.901 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:53:02.901 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:02.901 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:02.901 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:53:02.901 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:02.901 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:02.901 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:53:02.901 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:03.901 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:03.901 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:53:03.901 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:03.901 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:03.901 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:53:03.901 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:03.901 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:03.901 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:53:03.901 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:04.901 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:04.901 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:53:04.901 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:04.901 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:04.901 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:53:04.901 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:04.901 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:04.901 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:53:04.901 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:05.901 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:05.901 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:53:05.901 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:05.901 (1B78) IO TX: AT+CMGF=1[0D]
24/10/2015 07:53:05.921 (1B78) IO RX: [0D][0A]OK[0D][0A]
24/10/2015 07:53:05.921 (0F98) TAG ==> (0.027) Tag(0.0.0.0).WriteValue (07:53:05.904) 1 = SUCCESS
24/10/2015 07:53:05.921 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:05.921 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:53:05.921 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:05.921 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:05.921 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:53:05.921 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:06.621 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:06.621 (1B78) IO TX: AT+CMGF=1[0D]
24/10/2015 07:53:06.641 (1B78) IO RX: [0D][0A]OK[0D][0A]
24/10/2015 07:53:06.641 (0F98) TAG ==> (0.026) Tag(0.0.0.0).WriteValue (07:53:06.602) 0 = SUCCESS
24/10/2015 07:53:06.841 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:06.841 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:53:06.841 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:06.891 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:06.891 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:53:06.891 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:06.891 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:06.891 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:53:06.891 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
log continued in second message
24/10/2015 07:53:07.891 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:07.891 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:53:07.891 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:07.891 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:07.891 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:53:07.891 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:07.891 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:07.891 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:53:07.891 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:08.891 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:08.891 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:53:08.891 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:08.891 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:08.891 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:53:08.891 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:08.891 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:08.891 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:53:08.891 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:08.901 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:08.901 (1B78) IO TX: AT+CMGF=1[0D]
24/10/2015 07:53:08.921 (1B78) IO RX: [0D][0A]OK[0D][0A]
24/10/2015 07:53:08.921 (0F98) TAG ==> (0.027) Tag(0.0.0.0).WriteValue (07:53:08.904) 1 = SUCCESS
24/10/2015 07:53:09.521 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:09.521 (1B78) IO TX: AT+CMGF=1[0D]
24/10/2015 07:53:09.541 (1B78) IO RX: [0D][0A]OK[0D][0A]
24/10/2015 07:53:09.541 (0F98) TAG ==> (0.026) Tag(0.0.0.0).WriteValue (07:53:09.490) 0 = SUCCESS
24/10/2015 07:53:09.841 (0F98) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:09.841 (0F98) DRIVER CheckParam: ERROR - Command 0 is not a read command!
24/10/2015 07:53:09.841 (0F98) TAG <== (0.000) Tag(0.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:09.891 (0F98) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:09.891 (0F98) DRIVER CheckParam: ERROR - Command 6 is not a read command!
24/10/2015 07:53:09.891 (0F98) TAG <== (0.000) Tag(6.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:09.891 (0F98) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
24/10/2015 07:53:09.891 (0F98) DRIVER CheckParam: ERROR - Command 5 is not a read command!
24/10/2015 07:53:09.891 (0F98) TAG <== (0.000) Tag(5.0.0.0).ReadValue = ERROR (hr=80070057)
24/10/2015 07:53:10.772 (0F98) DRIVER drvStopComm(0,0,0,0)
24/10/2015 07:53:10.772 (0F98) IOKIT Stopping physical layer thread…
24/10/2015 07:53:10.772 (0F98) IOKIT Waiting for termination of physical layer thread…
24/10/2015 07:53:12.010 (1B78) IOKIT TERMINATING…
24/10/2015 07:53:12.010 (1B78) IOKIT TERMINATED! (0 bytes sent, 0 bytes received)
24/10/2015 07:53:12.010 (1B78) IOKIT Request handler disabled
24/10/2015 07:53:12.010 (0F98) IOKIT Physical layer thread stopped!
Dear Amol,
You have to write in 2 tags:
Tag001 (N1=6)
Tag002 (N1=5)
You can use the Button’s OnRelease event for that. For exemple:
Tag001 = “9769747727”
Tag002 = “Message”
Sir I have done that
Tag 1 for (N1=6) mobile number
Tag 2 for (N1=5) message
tag 3 for (N1=0) to send message (for button release event)
With this setup I am able to send 1 message .But if i press and release button second or third time, Message does not get sent.
To send message again, I need to restart Elipse Application.
Please send your application to pgustavo@elipse.com.br.
I have just sent you an email
Hi pgustaco
Please support for me how to send the same content to many people at the same time !
Thanks you so much !
Dear @Amol_Raut,
Your application is writing the tags only once because you are using setpoints to write the tags.
You have to write by script, as the image below.
Dear @tieungunhi59,
Your question was answered in another post. Please follow the link below.
Thanks for help
Can move further with my project
Dear @pgustavo,
When I send multiple SMS using script as you suggested, all the message are delivered properly to recipients. But at the time of sending message, The Elipse scada system becomes very slow. When all ge message get sent , The scada system works properly.
Is there any way to avoid this.
My GSM_driver configuration is shown in picture. your help is needed to resolve same
27/11/2015 23:24:44.156 (1604) IO RX: [0D][0A]OK[0D][0A]
27/11/2015 23:24:44.156 (00C4) TAG ==> (0.030) Tag(0.0.0.0).WriteValue (23:24:31.476) 1 = SUCCESS
27/11/2015 23:24:44.156 (00C4) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:44.156 (1604) IO TX: AT+CMGS=“9769747727”[0D]
27/11/2015 23:24:44.187 (1604) IO RX: [0D][0A]>
27/11/2015 23:24:44.187 (00C4) TAG ==> (0.039) Tag(6.0.0.0).WriteValue (23:24:31.476) ‘9769747727’ = SUCCESS
27/11/2015 23:24:44.187 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:44.296 (1604) IO TX: Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015[1A]
27/11/2015 23:24:46.312 (1604) IO RX: TIMEOUT
27/11/2015 23:24:46.312 (00C4) DRIVER Command: ERROR - Error on SendReceive.
27/11/2015 23:24:46.312 (00C4) TAG ==> (2.117) Tag(5.0.0.0).WriteValue (23:24:31.476) ‘Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015’ = ERROR (hr=80004005)
27/11/2015 23:24:46.312 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:46.421 (1604) IO TX: Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015[1A]
27/11/2015 23:24:47.765 (1604) IO RX: [0D][0A]+CMGS: 16[0D][0A][0D][0A]OK[0D][0A]
27/11/2015 23:24:47.781 (00C4) TAG ==> (1.474) Tag(5.0.0.0).WriteValue (23:24:31.476) ‘Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015’ = SUCCESS
27/11/2015 23:24:47.781 (00C4) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:47.781 (1604) IO TX: AT+CMGF=1[0D]
27/11/2015 23:24:47.812 (1604) IO RX: [0D][0A]OK[0D][0A]
27/11/2015 23:24:47.812 (00C4) TAG ==> (0.030) Tag(0.0.0.0).WriteValue (23:24:31.476) 1 = SUCCESS
27/11/2015 23:24:47.812 (00C4) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:47.828 (1604) IO TX: AT+CMGS=“9769747727”[0D]
27/11/2015 23:24:47.843 (1604) IO RX: [0D][0A]>
27/11/2015 23:24:47.843 (00C4) TAG ==> (0.039) Tag(6.0.0.0).WriteValue (23:24:31.476) ‘9769747727’ = SUCCESS
27/11/2015 23:24:47.843 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:47.968 (1604) IO TX: Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015[1A]
27/11/2015 23:24:49.984 (1604) IO RX: TIMEOUT
27/11/2015 23:24:49.984 (00C4) DRIVER Command: ERROR - Error on SendReceive.
27/11/2015 23:24:49.984 (00C4) TAG ==> (2.130) Tag(5.0.0.0).WriteValue (23:24:31.476) ‘Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015’ = ERROR (hr=80004005)
27/11/2015 23:24:49.984 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:50.093 (1604) IO TX: Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015[1A]
27/11/2015 23:24:51.187 (1604) IO RX: [0D][0A]+CMGS: 17[0D][0A][0D][0A]OK[0D][0A]
27/11/2015 23:24:51.203 (00C4) TAG ==> (1.222) Tag(5.0.0.0).WriteValue (23:24:31.476) ‘Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015’ = SUCCESS
27/11/2015 23:24:51.203 (00C4) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:51.203 (1604) IO TX: AT+CMGF=1[0D]
27/11/2015 23:24:51.234 (1604) IO RX: [0D][0A]OK[0D][0A]
27/11/2015 23:24:51.234 (00C4) TAG ==> (0.030) Tag(0.0.0.0).WriteValue (23:24:31.476) 1 = SUCCESS
27/11/2015 23:24:51.234 (00C4) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:51.234 (1604) IO TX: AT+CMGS=“9769747727”[0D]
27/11/2015 23:24:51.265 (1604) IO RX: [0D][0A]>
27/11/2015 23:24:51.265 (00C4) TAG ==> (0.039) Tag(6.0.0.0).WriteValue (23:24:31.476) ‘9769747727’ = SUCCESS
27/11/2015 23:24:51.265 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:51.375 (1604) IO TX: Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015[1A]
27/11/2015 23:24:53.390 (1604) IO RX: TIMEOUT
27/11/2015 23:24:53.390 (00C4) DRIVER Command: ERROR - Error on SendReceive.
27/11/2015 23:24:53.390 (00C4) TAG ==> (2.116) Tag(5.0.0.0).WriteValue (23:24:31.476) ‘Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015’ = ERROR (hr=80004005)
27/11/2015 23:24:53.390 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:53.500 (1604) IO TX: Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015[1A]
27/11/2015 23:24:54.781 (1604) IO RX: [0D][0A]+CMGS: 18[0D][0A][0D][0A]OK[0D][0A]
27/11/2015 23:24:54.796 (00C4) TAG ==> (1.420) Tag(5.0.0.0).WriteValue (23:24:31.476) ‘Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015’ = SUCCESS
27/11/2015 23:24:54.796 (00C4) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:54.796 (1604) IO TX: AT+CMGF=1[0D]
27/11/2015 23:24:54.828 (1604) IO RX: [0D][0A]OK[0D][0A]
27/11/2015 23:24:54.828 (00C4) TAG ==> (0.030) Tag(0.0.0.0).WriteValue (23:24:31.476) 1 = SUCCESS
27/11/2015 23:24:54.828 (00C4) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:54.843 (1604) IO TX: AT+CMGS=“9769747727”[0D]
27/11/2015 23:24:54.875 (1604) IO RX: [0D][0A]>
27/11/2015 23:24:54.875 (00C4) TAG ==> (0.039) Tag(6.0.0.0).WriteValue (23:24:31.476) ‘9769747727’ = SUCCESS
27/11/2015 23:24:54.875 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:54.984 (1604) IO TX: Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015[1A]
27/11/2015 23:24:57.000 (1604) IO RX: TIMEOUT
27/11/2015 23:24:57.000 (00C4) DRIVER Command: ERROR - Error on SendReceive.
27/11/2015 23:24:57.000 (00C4) TAG ==> (2.120) Tag(5.0.0.0).WriteValue (23:24:31.476) ‘Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015’ = ERROR (hr=80004005)
27/11/2015 23:24:57.000 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:57.109 (1604) IO TX: Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015[1A]
27/11/2015 23:24:58.359 (1604) IO RX: [0D][0A]+CMGS: 19[0D][0A][0D][0A]OK[0D][0A]
27/11/2015 23:24:58.375 (00C4) TAG ==> (1.378) Tag(5.0.0.0).WriteValue (23:24:31.476) ‘Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015’ = SUCCESS
27/11/2015 23:24:58.375 (00C4) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:58.375 (1604) IO TX: AT+CMGF=1[0D]
27/11/2015 23:24:58.406 (1604) IO RX: [0D][0A]OK[0D][0A]
27/11/2015 23:24:58.406 (00C4) TAG ==> (0.030) Tag(0.0.0.0).WriteValue (23:24:31.476) 1 = SUCCESS
27/11/2015 23:24:58.406 (00C4) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:58.421 (1604) IO TX: AT+CMGS=“9769747727”[0D]
27/11/2015 23:24:58.437 (1604) IO RX: [0D][0A]>
27/11/2015 23:24:58.437 (00C4) TAG ==> (0.039) Tag(6.0.0.0).WriteValue (23:24:31.476) ‘9769747727’ = SUCCESS
27/11/2015 23:24:58.437 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:24:58.562 (1604) IO TX: Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015[1A]
27/11/2015 23:25:00.578 (1604) IO RX: TIMEOUT
27/11/2015 23:25:00.578 (00C4) DRIVER Command: ERROR - Error on SendReceive.
27/11/2015 23:25:00.578 (00C4) TAG ==> (2.131) Tag(5.0.0.0).WriteValue (23:24:31.476) ‘Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015’ = ERROR (hr=80004005)
27/11/2015 23:25:00.578 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:00.687 (1604) IO TX: Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015[1A]
27/11/2015 23:25:02.015 (1604) IO RX: [0D][0A]+CMGS: 20[0D][0A][0D][0A]OK[0D][0A]
27/11/2015 23:25:02.031 (00C4) TAG ==> (1.456) Tag(5.0.0.0).WriteValue (23:24:31.476) ‘Prepainting line Hoist Machine SKID 01 HOIST HR2T02 Wire rope replacement Activity Pending. target dt. is 26/11/2015’ = SUCCESS
27/11/2015 23:25:02.031 (00C4) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:02.031 (1604) IO TX: AT+CMGF=1[0D]
27/11/2015 23:25:02.062 (1604) IO RX: [0D][0A]OK[0D][0A]
27/11/2015 23:25:02.062 (00C4) TAG ==> (0.030) Tag(0.0.0.0).WriteValue (23:24:31.477) 1 = SUCCESS
27/11/2015 23:25:02.062 (00C4) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:02.078 (1604) IO TX: AT+CMGS=“9769747727”[0D]
27/11/2015 23:25:02.093 (1604) IO RX: [0D][0A]>
27/11/2015 23:25:02.093 (00C4) TAG ==> (0.039) Tag(6.0.0.0).WriteValue (23:24:31.477) ‘9769747727’ = SUCCESS
27/11/2015 23:25:02.093 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:02.218 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:04.234 (1604) IO RX: TIMEOUT
27/11/2015 23:25:04.234 (00C4) DRIVER Command: ERROR - Error on SendReceive.
27/11/2015 23:25:04.234 (00C4) TAG ==> (2.131) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = ERROR (hr=80004005)
27/11/2015 23:25:04.234 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:04.359 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:05.593 (1604) IO RX: [0D][0A]+CMGS: 21[0D][0A][0D][0A]OK[0D][0A]
27/11/2015 23:25:05.609 (00C4) TAG ==> (1.386) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = SUCCESS
27/11/2015 23:25:05.609 (00C4) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:05.609 (1604) IO TX: AT+CMGF=1[0D]
27/11/2015 23:25:05.640 (1604) IO RX: [0D][0A]OK[0D][0A]
27/11/2015 23:25:05.640 (00C4) TAG ==> (0.030) Tag(0.0.0.0).WriteValue (23:24:31.477) 1 = SUCCESS
27/11/2015 23:25:05.640 (00C4) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:05.656 (1604) IO TX: AT+CMGS=“9769747727”[0D]
27/11/2015 23:25:05.687 (1604) IO RX: [0D][0A]>
27/11/2015 23:25:05.687 (00C4) TAG ==> (0.039) Tag(6.0.0.0).WriteValue (23:24:31.477) ‘9769747727’ = SUCCESS
27/11/2015 23:25:05.687 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:05.812 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:07.828 (1604) IO RX: TIMEOUT
27/11/2015 23:25:07.828 (00C4) DRIVER Command: ERROR - Error on SendReceive.
27/11/2015 23:25:07.828 (00C4) TAG ==> (2.139) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = ERROR (hr=80004005)
27/11/2015 23:25:07.828 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:07.953 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:09.421 (1604) IO RX: [0D][0A]+CMGS: 22[0D][0A][0D][0A]OK[0D][0A]
27/11/2015 23:25:09.437 (00C4) TAG ==> (1.614) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = SUCCESS
27/11/2015 23:25:09.437 (00C4) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:09.437 (1604) IO TX: AT+CMGF=1[0D]
27/11/2015 23:25:09.468 (1604) IO RX: [0D][0A]OK[0D][0A]
27/11/2015 23:25:09.468 (00C4) TAG ==> (0.030) Tag(0.0.0.0).WriteValue (23:24:31.477) 1 = SUCCESS
27/11/2015 23:25:09.468 (00C4) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:09.484 (1604) IO TX: AT+CMGS=“9769747727”[0D]
27/11/2015 23:25:09.500 (1604) IO RX: [0D][0A]>
27/11/2015 23:25:09.500 (00C4) TAG ==> (0.039) Tag(6.0.0.0).WriteValue (23:24:31.477) ‘9769747727’ = SUCCESS
27/11/2015 23:25:09.500 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:09.640 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:11.656 (1604) IO RX: TIMEOUT
27/11/2015 23:25:11.656 (00C4) DRIVER Command: ERROR - Error on SendReceive.
27/11/2015 23:25:11.656 (00C4) TAG ==> (2.145) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = ERROR (hr=80004005)
27/11/2015 23:25:11.656 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:11.781 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:13.796 (1604) IO RX: TIMEOUT
27/11/2015 23:25:13.796 (00C4) DRIVER Command: ERROR - Error on SendReceive.
27/11/2015 23:25:13.796 (00C4) TAG ==> (2.141) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = ERROR (hr=80004005)
27/11/2015 23:25:13.796 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:13.921 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:14.328 (1604) IO RX: [0D][0A]+CMGS: 23[0D][0A][0D][0A]OK[0D][0A]
27/11/2015 23:25:14.343 (00C4) TAG ==> (0.551) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = SUCCESS
27/11/2015 23:25:14.343 (00C4) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:14.343 (1604) IO TX: AT+CMGF=1[0D]
27/11/2015 23:25:14.375 (1604) IO RX: [0D][0A]OK[0D][0A]
27/11/2015 23:25:14.375 (00C4) TAG ==> (0.030) Tag(0.0.0.0).WriteValue (23:24:31.477) 1 = SUCCESS
27/11/2015 23:25:14.375 (00C4) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:14.390 (1604) IO TX: AT+CMGS=“9769747727”[0D]
27/11/2015 23:25:14.406 (1604) IO RX: [0D][0A]>
27/11/2015 23:25:14.406 (00C4) TAG ==> (0.038) Tag(6.0.0.0).WriteValue (23:24:31.477) ‘9769747727’ = SUCCESS
27/11/2015 23:25:14.406 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:14.531 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:16.546 (1604) IO RX: TIMEOUT
27/11/2015 23:25:16.546 (00C4) DRIVER Command: ERROR - Error on SendReceive.
27/11/2015 23:25:16.546 (00C4) TAG ==> (2.130) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = ERROR (hr=80004005)
27/11/2015 23:25:16.546 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:16.671 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:18.000 (1604) IO RX: [0D][0A]+CMGS: 24[0D][0A][0D][0A]OK[0D][0A]
27/11/2015 23:25:18.015 (00C4) TAG ==> (1.475) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = SUCCESS
27/11/2015 23:25:18.015 (00C4) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:18.015 (1604) IO TX: AT+CMGF=1[0D]
27/11/2015 23:25:18.046 (1604) IO RX: [0D][0A]OK[0D][0A]
27/11/2015 23:25:18.046 (00C4) TAG ==> (0.030) Tag(0.0.0.0).WriteValue (23:24:31.477) 1 = SUCCESS
27/11/2015 23:25:18.046 (00C4) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:18.062 (1604) IO TX: AT+CMGS=“9769747727”[0D]
27/11/2015 23:25:18.078 (1604) IO RX: [0D][0A]>
27/11/2015 23:25:18.078 (00C4) TAG ==> (0.039) Tag(6.0.0.0).WriteValue (23:24:31.477) ‘9769747727’ = SUCCESS
27/11/2015 23:25:18.078 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:18.218 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:20.234 (1604) IO RX: TIMEOUT
27/11/2015 23:25:20.234 (00C4) DRIVER Command: ERROR - Error on SendReceive.
27/11/2015 23:25:20.234 (00C4) TAG ==> (2.144) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = ERROR (hr=80004005)
27/11/2015 23:25:20.234 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:20.359 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:21.796 (1604) IO RX: [0D][0A]+CMGS: 25[0D][0A][0D][0A]OK[0D][0A]
27/11/2015 23:25:21.812 (00C4) TAG ==> (1.590) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = SUCCESS
27/11/2015 23:25:21.812 (00C4) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:21.812 (1604) IO TX: AT+CMGF=1[0D]
27/11/2015 23:25:21.843 (1604) IO RX: [0D][0A]OK[0D][0A]
27/11/2015 23:25:21.843 (00C4) TAG ==> (0.030) Tag(0.0.0.0).WriteValue (23:24:31.477) 1 = SUCCESS
27/11/2015 23:25:21.843 (00C4) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:21.859 (1604) IO TX: AT+CMGS=“9769747727”[0D]
27/11/2015 23:25:21.890 (1604) IO RX: [0D][0A]>
27/11/2015 23:25:21.890 (00C4) TAG ==> (0.039) Tag(6.0.0.0).WriteValue (23:24:31.477) ‘9769747727’ = SUCCESS
27/11/2015 23:25:21.890 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:22.015 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:24.031 (1604) IO RX: TIMEOUT
27/11/2015 23:25:24.031 (00C4) DRIVER Command: ERROR - Error on SendReceive.
27/11/2015 23:25:24.031 (00C4) TAG ==> (2.138) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = ERROR (hr=80004005)
27/11/2015 23:25:24.031 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:24.156 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:25.390 (1604) IO RX: [0D][0A]+CMGS: 26[0D][0A][0D][0A]OK[0D][0A]
27/11/2015 23:25:25.406 (00C4) TAG ==> (1.380) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = SUCCESS
27/11/2015 23:25:25.406 (00C4) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:25.406 (1604) IO TX: AT+CMGF=1[0D]
27/11/2015 23:25:25.437 (1604) IO RX: [0D][0A]OK[0D][0A]
27/11/2015 23:25:25.437 (00C4) TAG ==> (0.030) Tag(0.0.0.0).WriteValue (23:24:31.477) 1 = SUCCESS
27/11/2015 23:25:25.437 (00C4) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:25.453 (1604) IO TX: AT+CMGS=“9769747727”[0D]
27/11/2015 23:25:25.468 (1604) IO RX: [0D][0A]>
27/11/2015 23:25:25.468 (00C4) TAG ==> (0.038) Tag(6.0.0.0).WriteValue (23:24:31.477) ‘9769747727’ = SUCCESS
27/11/2015 23:25:25.468 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:25.609 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:27.625 (1604) IO RX: TIMEOUT
27/11/2015 23:25:27.625 (00C4) DRIVER Command: ERROR - Error on SendReceive.
27/11/2015 23:25:27.625 (00C4) TAG ==> (2.145) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = ERROR (hr=80004005)
27/11/2015 23:25:27.625 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:27.750 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:28.937 (1604) IO RX: [0D][0A]+CMGS: 27[0D][0A][0D][0A]OK[0D][0A]
27/11/2015 23:25:28.953 (00C4) TAG ==> (1.335) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = SUCCESS
27/11/2015 23:25:28.953 (00C4) TAG Tag(0.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:28.953 (1604) IO TX: AT+CMGF=1[0D]
27/11/2015 23:25:28.984 (1604) IO RX: [0D][0A]OK[0D][0A]
27/11/2015 23:25:28.984 (00C4) TAG ==> (0.030) Tag(0.0.0.0).WriteValue (23:24:31.477) 1 = SUCCESS
27/11/2015 23:25:28.984 (00C4) TAG Tag(6.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:29.000 (1604) IO TX: AT+CMGS=“9769747727”[0D]
27/11/2015 23:25:29.015 (1604) IO RX: [0D][0A]>
27/11/2015 23:25:29.015 (00C4) TAG ==> (0.039) Tag(6.0.0.0).WriteValue (23:24:31.477) ‘9769747727’ = SUCCESS
27/11/2015 23:25:29.015 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:29.156 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
27/11/2015 23:25:31.171 (1604) IO RX: TIMEOUT
27/11/2015 23:25:31.171 (00C4) DRIVER Command: ERROR - Error on SendReceive.
27/11/2015 23:25:31.171 (00C4) TAG ==> (2.142) Tag(5.0.0.0).WriteValue (23:24:31.477) ‘Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015’ = ERROR (hr=80004005)
27/11/2015 23:25:31.171 (00C4) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
27/11/2015 23:25:31.296 (1604) IO TX: Prepainting line Hoist Machine TRANSMISSION-1 UNLOAD HR2T03 Wire rope replacement Activity Pending. target dt. is 27/11/2015[1A]
Dear Amol,
Please send the complete log file attached to my e-mail: pgustavo@elipse.com.br.
email sent
please check and revert back
Dear Amol,
According to the log file, the slowness occurs because the modem does not respond to all commands, which is causing a lot of timeout occurrences like this you can see below:
07/11/2015 22:25:18.812 (1250) IO TX: AT+CMGS="9769747727"[0D]
07/11/2015 22:25:18.843 (1250) IO RX: [0D][0A]>
07/11/2015 22:25:18.843 (0B80) TAG ==> (0.038) Tag(6.0.0.0).WriteValue (22:25:18.710) '9769747727' = SUCCESS
07/11/2015 22:25:18.843 (0B80) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
07/11/2015 22:25:18.906 (1250) IO TX: Prepainting line Venus Lifter cylinder Seal kit replacement Activity Done[1A]
07/11/2015 22:25:20.921 (1250) IO RX: TIMEOUT
07/11/2015 22:25:20.921 (0B80) DRIVER Command: ERROR - Error on SendReceive.
07/11/2015 22:25:20.921 (0B80) TAG ==> (2.073) Tag(5.0.0.0).WriteValue (22:25:15.713) 'Prepainting line Venus Lifter cylinder Seal kit replacement Activity Done' = ERROR (hr=80004005)
07/11/2015 22:25:20.921 (0B80) TAG Tag(5.0.0.0).Validate = SUCCESS (type=10;flags=0)
07/11/2015 22:25:20.984 (1250) IO TX: Prepainting line Venus Lifter cylinder Seal kit replacement Activity Done[1A]
07/11/2015 22:25:21.671 (1250) IO RX: [0D][0A]+CMGS: 129[0D][0A][0D][0A]OK[0D][0A]
07/11/2015 22:25:21.687 (0B80) TAG ==> (0.776) Tag(5.0.0.0).WriteValue (22:25:15.713) 'Prepainting line Venus Lifter cylinder Seal kit replacement Activity Done' = SUCCESS
What is the solution ?
Shall I increase the baudrate or do you suggest replacing GSM modem.
I want to know one more thing
Will upgrading Hardware improve SCADA performance ?
My present computer setup is
AMD phenom II X2 processor
2 GB RAM
250 GB (7200 RPM) HDD
I am running Elipse SCADA with around 3000 tags.
operating system is Window 7