How to communicate energy meter (conserv make Em6400,rs 485 communication)with Elipse scada

How to communicate energy meter (conserv make Em6400,rs 485 communication)with Elipse scada

@Kannan_Suresh, good afternoon.

According to the manufacturer’s manual, the factory settings are (see page 40):

"7.3. Factory Settings

  • Communication Protocol: Modbus – RTU

Baud Rate: 9600 bps
Data bits: 8
Stop bits: 1
Parity: Even

  • Data type: 32-bit Float (Real) for all parameters unless otherwise specified.

Except for parameter:

  • INTR (Number of interruptions (Outages) in RMS parameter blocks) – unsigned 32-
    bit integer data type.
  • RunSec (Run Seconds in Integrated block) – unsigned 32-bit integer data type.
  • Data Format: Direct reading from the meter, no scaling is required.

  • Modbus Function code: 03 (Read)"


In this case , you should use the Modbus Master driver. Download Link.

In “Modbus” tab , configure Modbus RTU .

In the “Setup” tab , set the physical layer as Serial .

In the “Serial” tab , choose the same parameters configured on the meter.

To configure the IO tags, use the meter address map available here and the driver documentation provided with the DLL.

Related articles:

I hope it helps.

Hi…as per my knowledge you need a Modbus RTU/Modbus TCP gateway such as Moxa MB3180 or a HMS Anybus gateway to convert between the two protocols. Then you just have to add a Modbus Channel to WinCC, configure it to the gateway IP address and slave number and add the tags you want to read.